Bradford White Water Heater Troubleshooting Guide

On this page (6 sections)

The Short Answer: First identify which type of Bradford White you have. Atmospheric gas tanks report faults through a flashing LED on the gas control, and older mechanical controls have no light at all. Electric tanks have no diagnostic light. Heat-pump and tankless models show codes on a display. A leaking tank means replacement. Most other faults are repairable.

Atmospheric gas tanks (Defender)

Look at the gas control on the front of the tank. Bradford White has used several controls. The White Rodgers mechanical control has no status light and uses a thermocouple. The White Rodgers electronic, Honeywell V1 and Honeywell V2 controls have a status LED and use a thermopile. Bradford White’s service manual gives these meanings for the LED controls:

Status light Meaning
Off Pilot not lit, control unpowered
One flash every few seconds Pilot lit, burner off. Normal
One flash every second Burner on, heating. Normal
Solid on after turning the knob to OFF Shutdown. Wait for it to go out before relighting
Two flashes, pause Low thermopile voltage or weak pilot signal
Three flashes, pause (Honeywell V1) Insufficient water heating; sensor out of calibration or control fault
Four flashes, pause Excessive tank temperature or temperature cut-out
Five flashes, pause Sensor, electronics or gas valve fault (Honeywell V1: temperature sensor fault)
Six flashes, pause (Honeywell V1) Water leak detected by an accessory leak module
Seven flashes, pause (Honeywell V1) Gas control electronic fault
Eight flashes, pause (Honeywell V1) Pilot still on with the knob at OFF. The control needs replacing

Where to go next:

Four, five, seven and eight flashes are gas control or sensor faults that a technician needs to diagnose. Don’t keep cycling the control.

Electric tanks

Standard Bradford White electric tanks have two elements and two thermostats. A high-temperature limit sits on the upper thermostat. No hot water usually points to the breaker, the high limit, or the upper circuit. Hot water that runs out quickly usually points to the lower circuit. You can check and reset the breaker once. Resetting the high limit and testing the parts happen behind the electrical covers and need a technician. See Bradford White electric not heating up.

Lukewarm water

Bradford White’s chart for not enough hot water covers the temperature setting, cold inlet water, high demand, sizing, calibration and the dip tube. See Bradford White not hot enough.

Leaks

Where Usually
Top of the tank Connector, nipple, anode fitting or relief valve. See leaking from top
Relief valve discharge pipe Pressure or temperature problem. Never cap it
Drain valve Valve seat or washer
Electric element or thermostat cover Element gasket or tank. See leaking at the thermostat panel
Out of the insulation or base, fittings dry Tank. Replace the heater

Models with a display

AeroTherm heat-pump models, Infiniti tankless units and some power-vent models show codes on a display or controller, and some sound an alert. Look up codes in the manual for your exact model. Bradford White explains how to find a manual from the model and serial number (opens in a new tab). See also Bradford White beeping.

Frequently Asked Questions

Q: How do I find my Bradford White’s age? A: The serial number on the rating plate encodes the manufacture date. See how old is my water heater.

Q: Do these LED meanings apply to Bradford White power-vent models? A: Not necessarily. The table comes from the service manual for atmospheric Defender models. Power-vent and high-efficiency models use different controls with their own code lists.

Q: Is a Bradford White gas control the same as a Rheem or A. O. Smith one? A: No. Even when a similar control maker is involved, the flash codes and parts are specific to the heater manufacturer and model. Use Bradford White’s documentation.

Before you call a technician

Write down

  • The heater. Photograph the rating plate: brand, full model number, serial number, and fuel. The serial number usually encodes the manufacture date.
  • The exact code. Photograph the display, or count the flashes and the pause between groups. Note whether the code returns after one reset.
  • The water. From a dry spot, note the highest wet point, whether it drips or flows, and whether it is hot. A photo of the top fittings, drain valve, and relief pipe helps.

Stop and get help if

  • Gas or rotten-egg smell, or a CO alarm: leave now and call the gas utility or 911 from outside. Do not use switches or try to find the source.
  • Water flowing, hot discharge, a wet electrical cover, or water near the burner: keep clear and shut the cold inlet only if it is safely reachable.
  • A breaker that trips again, or a scorched or melted smell: leave it off.
  • A burner bang, flames outside the burner area, soot, or a smell of exhaust: turn the heater off at its control and do not relight it.
  • Never cap the relief valve, bypass a safety switch, or open gas, electrical, or sealed combustion parts.

Manuals and supporting references

These links distinguish general safety information from model-specific documentation. A manual directory helps you locate your unit’s instructions; it does not establish that every model uses the same parts, codes, or test values.

Editorial standards and corrections · Prepare a useful service request